Wiring – Inground Conduit Box for Driveway Snow Melting

conduitradiant-heatingwiring

I'm installing snow melting cables into a concrete and stone paver driveway. It requires 5 mats rated at 25 Amps and 6000 watts. I also need a 6th small run of heating wire to cover the full area. The cold leads (non-resistive conductor cable) are 10/3 and 20 feet long.

So to get it to my basement I need an in-ground conduit box to run the 6 cables into then splice them with 10/3 NMWU in the box and run those through one or 2 conduits to the house panel.

So my first questions are about the conduit sizes and pulling the wires.
For the cold leads to the conduit box …

Will 1/2" PVC conduit be to hard to pull through (3 to 15 feet, 2x 90 elbows)?

Is 3/4" overkill?

Can I get 6x – 10/3 wires easily through one 2" conduit? (3x 90 elbows @ 15-20 feet).

Fill table says 63 max for 10/3 conductors and I will have 6×3 =18 plus ground and sheathing.

Ontario, Canada

Snow Melting Cable Dissection

Best Answer

If in only 1 pipe is there a derate for the number of current carrying conductors? In the U.S. I would be using thhn/thwn wire, but with 25 amp actual draw I would need to upsize the wire to #8 because 125% of 25 is 31.25a . 1-1/2 rigid pvc would allow 18 #8 , i would not try to pull multi conductor cables through conduit it costs more and is not needed since you are running conduit. Thhn/thwn wire is rated for wet locations and would cost less than NMWU. And as Isherwood mentioned since the splices are going to be below grade they need to be listed for wet / direct burial. On a side note are you going to put insulation under the mats? It will really help with power consumption that is going to be an expensive way to melt the ice and snow.