Wiring – Shared neutral with two separate breakers

circuit breakerwiring

As I continue to make sense of the wiring in home, I have come across some shared neutral configurations. In one, I find two breakers that have been connected to one NM-3 line i.e. black and red are each connected to a separate breaker (on the same side of the box.) As I understand from here and other references, this is OK but it should be on a 'split-phase double breaker'.

First question: Am I right that this configuration is incorrect and should be fixed?

Second question: This suggests that these configurations are problematic for AFCI installations. I want to upgrade my breakers to AFCI. Will this kind of thing be an issue?

Lastly, for anyone so inclined, I have a Cutler-Hammer CH style board. If this needs to be fixed, which breakers would be acceptable?

Best Answer

As long as the ungrounded (hot) conductors of the circuit are fed by different legs of the service, then there's no problem with the wiring. According to modern codes, the breakers need to at least have a handle tie. However, since the installation presumably predates the code, it does not have to be changed (unless you're doing work that requires it).

If you want to install AFCI breakers, you'll simply have to replace the two breakers with a double pole AFCI breaker.