A sub panel must have the neutral and ground isolated. Panels come with a very long, rather thick (about 1/4 x 20) green bonding screw that connects the neutral bar to the can in the case of a primary panel. You don't get a neutral from your utility, you create one with that bonding screw.
Sub panels should be fed with 3 insulated conductors of appropriate size, and a ground that need not be insulated (but can be, if you want). So the first part of your question is, yes, that sub panel must be grounded, but the grounding conductor should be attached to the can using a ground lug, not by landing it to the neutral bar.
Sub panels must also have a fused disconnect, which means they need to be fed from a breaker, and there can't be anything else on that breaker. Don't double tap. You have two options here:
- Increase the size of the existing sub panel
- Put in a new double pole breaker in the existing sub panel and use that to feed your new sub panel. Land the circuits you had to pull out of the existing sub panel into the new one.
As others have noted, you need to watch your loads. If all you need are a few convenience receptacles or a lighting circuit, you should probably be o.k. (hard to tell with what you've given).
Either way, get an amprobe and look at what each incoming phase is pulling in your existing sub panel prior to doing anything. Make sure everything is on when you do. If it's only pulling 25 - 30A on average, you should be o.k. to add a small 8 circuit sub panel. Since it's directly in the line of sight with the existing sub panel, the new sub panel need not have a main breaker since the means of disconnect is right next to it.
A six to eight circuit sub panel runs about $80 without breakers, they typically start at 50A, but you don't have to feed them with 50A. You could feed it from a 30A breaker if all you want are convenience receptacles and lights.
Here is an amprobe being used:
(source: amprobe.com)
Do that on your sub panel first (one phase at a time) just to be sure you have room to add more. If not, you need to replace your existing sub panel, and an electrician is really your best bet there.
Another good thing to do is measure the draw of the circuits you'll have to move to the sub panel in order to make room for the breaker that will feed it. Obviously, you want to move the circuits drawing the least to the new panel in the end. Some re-arranging might be needed to make that happen.
Since this is a garage, take care what you connect to the sub panel. If you are going to be powering something like a compressor (or anything else with a decent sized motor), carefully consider the locked rotor amperage when determining the load. It will be printed on the motor.
Finally, if any of this sounds overwhelming, call an electrician. If you get into any kind of trouble, call an electrician.
If you use a 100A breaker your main in the mobile home you will need #3 copper wire to feed the sub the sub panel. A 60 Amp breaker in the main panel should provide enough power from the loads listed this would require #6 copper wire.
You will need to run both hots a ground and neutral. In the sub the ground and neutral buses need to be isolated. Many times Panels come with the buses connected the connection will need to be removed or you can add a grounding buss screwed into the metal of the panel. (Make sure there is not a connection from the original buses to the box.)
I am hoping you will be living in the tiny house while remodel work is completed on the mobile. If both the mobile and the tiny house are used at the same time you may trip the main. If you trip the main you may have to do things like turn the AC off while the cook top is in use to prevent the main from tripping.
Best Answer
The NEC requires 30" of space for any Panel, but it does come with a lot of exceptions. One is door swings you must be able to the door 90 degrees to access the breakers. Seconfd it requires 30" but the panel does not have to be center of the space. Third panels can share the 30" space.
Also there are requirements for clearances. See attached.
Good luck