In my garage I have wiring for a 240V outlet. It is a four-wire setup (two hots, one neutral and one ground). It is set up on a 20 ampere double breaker in the circuit breaker box. I want to remove that outlet and install two 120V receptacles in its place. I plan to run each of the hot wires to the hot side of outlet 1 and 2 inside one electrical box. My plan was to split the neutral inside the box, and run it to the neutral side of outlets 1 and 2, and do the same thing with the ground.

I have researched this issue, but I've come up with conflicting answers. This answer seems to suggest that this would be acceptable since it is already on a 20 ampere, double breaker:

Can two circuits share a neutral?

Best Answer

Yes, you can certainly do this. It is referred to as a Multi-Wire Branch Circuit. The two hot legs share the neutral. It is quite common.

Note: Make sure you pigtail the neutral and ground wires, do NOT daisy chain them through the receptacles.

Here is a pertinent National Electrical Code reference:

210.4 Multiwire Branch Circuits.

(A) General. Branch circuits recognized by this article shall be permitted as multiwire circuits. A multiwire circuit shall be permitted to be considered as multiple circuits. All conductors of a multiwire branch circuit shall originate from the same panelboard or similar distribution equipment.

Informational Note No. 2: See 300.13(B) for continuity of grounded conductors on multiwire circuits.

(B) Disconnecting Means. Each multiwire branch circuit shall be provided with a means that will simultaneously disconnect all ungrounded conductors at the point where the branch circuit originates.

Informational Note: See 240.15(B) for information on the use of single-pole circuit breakers as the disconnecting means.

(C) Line-to-Neutral Loads. Multiwire branch circuits shall supply only line-to-neutral loads.

Exception No. 1: A multiwire branch circuit that supplies only one utilization equipment.

Exception No. 2: Where all ungrounded conductors of the multiwire branch circuit are opened simultaneously by the branch-circuit overcurrent device.

Good luck!