Breaker feeding an electric heater trips after one minute

circuit breaker

I purchased a Comfort Zone Heater. Model CZ230ER. It is a 7,500 watt 240V unit.
This was installed with 10/2 wire to a brand new 30 amp breaker. Once the heater has been running for about a minute it trips the breaker. I have verified there are no shorts.

I do have it about 60 feet from the panel and my wire conduit was only 25 feet long. The connections are made using wire nuts mounted in a metal box.

Any thoughts?

Best Answer

As noted by isherwood, you are pulling too much power. 7,500 W /240 V = 31.25 A on a 30 A circuit. Circuit breakers are typically designed to handle a somewhat higher than rated current for a short time - e.g., motor startup, a really high current (e.g., hundreds of Amps on a 30 A circuit) for an extremely short time, and a moderate overage for a moderate amount of time. This actually matches well with another rule: continuous loads should not exceed 80% of the rated circuit. In the case of 30 A, that means your continuous load should be no more than 24 A = 7,200 W.

So this is actually normal operation.

You need either a slightly smaller heater or a larger breaker with matching appropriately sized wiring.