Electrical – Adding 240v (NEMA 14-50) outlet right behind breaker panel

120-240vcode-complianceelectricalgarage

The breaker panel is on the outside wall, right next to my garage. I want to install a 240v outlet right behind the panel, thru the wall.

If i open the panel, there are those round metal covers that can be popped to run cables into the box.
Removing one shows the back of the interior drywall. ( since the breaker panel is recessed into the exterior wall)

Idea is simple. Add a 50amp breaker and just drill thru the drywall, run the appropriate cables (about 3 feet) thru the hole and straight into one of these:

Levinton 50 Amp, 125/250 Volt, NEMA 14-50R, 3P, 4W, Surface Mounted Receptacle

No wires would be exposed.

Would this be against code or any safety hazards that i need to be aware of?

Best Answer

You can do this it takes a simple bushing or clamp from the main panel. Since the cable is breaker protected as long as it is protected going out of the panel and into the new one it is code compliant. Well if you have a permit,