Are non-GFCI outlets that are downstream of a GFCI outlet ground fault protected if they are fed from the GFCI outlet's load side?

If those non-GFCI downstream outlets were not fed from the GFCI outlet's load side but rather just had their hot, neutral and ground wires spliced to those feeding the GFCI outlet, would the effect be the same as if there was no GFCI outlet on the circuit at all?

Best Answer

Yes, that is the entire purpose of the load terminals of the GFCI. You can imagine that the protection element of the GFCI extends both to its receptacles, and then just imagine the load pair as another "receptacle".

As to the second part, yes, if you just connect the terminals together "before" the GFCI protection is in place, the GFCI will have no effect - remember, it can only sense problems on its own receptacles and its load terminals.