Electrical – MWBC on Two Breakers: Is It Possible?

electrical

Has it ever been acceptable for a multi wire branch circuit to be on 2 separate breakers? My house, which was built in the mid 90s, has the dishwasher and the disposal on the same 12/3 cable, but not on a common trip breaker.

I'm going to replace the breaker, but I'm just curious if this was ever allowed.

Best Answer

Yes it is allowed, up through the 2020 NEC section 240.15(B)(1) single pole 120/240v breakers with handle ties are still allowed when the MWBC only feeds line to neutral loads.

I don't have my old books, but it wasn't until the 2000's that the common trip requirements entered the code, but even then your local authority may have not have immediately adopted the code or that section immediately upon publication. For instance 3 states are still using the 2008, four cycles behind.