Electrical – How to add arc-fault protection to circuits in this panel

circuit breakerelectricalelectrical-panel

enter image description here

In my sub-panel that services the home I have 4 separate 20 amp circuit breakers all strapped together to trip all if one trips. On these individual circuits are the garbage disposal, clothes washer, dishwasher and all GFCI circuits? I want to install arc fault breakers but need more slots or room. I would like to remove the 30 amp and 50 amp breakers and install tandem 30/20 and 50/20 and use the strapped together circuits on those 20 amp tandems; is this possible?

Best Answer

Any electrician who looks at this would consider that subpanel 'maxed out' ... Not necessarily due to the technicalities of the code to squeeze another circuit or two in with complex tandems but because of the amount of wire packed into that small box and the extreme of things taken to extremes - meaning the multitude of tandem breakers. Generally tandems are used for squeezing in 'one more' or properly upgrading a bath or kitchen on a tight panel. While possible to expand this box is a bit fully loaded as it is.

I would suggest getting a larger subpanel and trying to keep as much as possible as single, standard breakers. You can keep the feed wire and originating circuit breaker (in other panel) the same as long as you're not planning on adding more load. But a new metal panel box is going to be a similar price to a number of $20-30 complex tandems and tandem arc fault breakers.

Here's a subpanel for $75