Electrical – Can you wire a 30A 2P standard circuit breaker “downstream” from a 60A GFCI 2p circuit breaker

circuit breakercode-complianceelectricalgfciwiring

Will this still provide GFCI protection? Is this against code? Does this represent a hazard?

I have a subpanel with a 60A GFCI circuit breaker, that I want to use that to feed to 2 30a 240v receptacles. I'm looking to have GFCI protection on the lines, but also make sure the lines are protected for their rating.

Best Answer

This will work fine. The GFI protection is on the feeder side so everything downstream will be protected.

Out of curiosity, why the need for GFCI protection?