Electrical Wiring – How to Handle Overloaded Circuits with Too Many Lights and Receptacles

circuit breakerelectricalwiring

Recently during a storm a circuit breaker switched off half of our home's lights and sockets. Thinking it was due to moisture we waited for the house to dry and then reset the breaker. It would stay on for a while but then flip back off. Finally it would no longer switch on. We called an electrician who said there was a short but it would require troubleshooting to identify the exact location. He offered us two options:

  1. Troubleshoot the short only ($350)
  2. Split the circuit ($1200)

We counted all the lights and receptacles on the circuit and found 24. The 15A breaker should only support a load of 1400W (15A * 120V = 1800W * 80% max load). So it definitely seems there are too many junctions on the one circuit.

Is it possible to split the circuit without running additional wire through the house? The electrician seemed to indicate it was but I wasn't clear on his explanation. He mentioned using pigtails but I'm unsure if he meant pigtail connections or AFCI breakers.

I don't mind spending more money but I'd like to get the root problem solved. Would splitting the circuit and using two 20A breakers be sufficient? If so, what changes to the wiring are necessary?

EDIT:

This is the breaker box:
breaker box

This is the circuit breaker in question (OFF is the shorted circuit):
circuit breaker in question

Best Answer

You will need at least 1 new circuit, and to break the circuit and install that new 15amp circuit (I am guessing the wiring is 14 awg). You can get things to work by removing some of the load but you probably have figured that out.

If you have room adding a breaker is not that hard but you will need to do some reading and ask more questions.

You cannot use 20 amp breakers on 14awg wire--you have to stay with 15 amp breakers unless the wiring is 12awg.

I doubt you have a short just a simple overload, so you will need to run a new circuit.

To prove it’s not shorted, turn the lights off, unplug things, then reset the breaker. Now turn each room on then off and start plugging things in. If a single device like a electric heater is on the circuit, just leave that unplugged and everything else will probably work.