Electrical – Connect neutrals together in 3-gang box (load side) with 3x 3-way switches

electrical

I have 2x 3-gang boxes, each with 3x 3-way switches in each box. All are on the same 15A breaker.

I have wired them together and I'm just connecting the switches now. I have:

                 --------              ---------
BREAKER --14/2-- |3x-3WAY| --3x14/3-- |3x 3-WAY| ---3x14/2-- LIGHTS
                 ---------             ---------

The 3-gang boxes are connected with 3 runs of 14/3 cable.

My question is: should I splice the neutrals together (and the grounds) at the second 3-gang box (load side)? It seems like it doesn't matter, since they could just as well be going to 3x 1-gang boxes on the load side in which case they would NOT be connected.

To clarify – I'm not asking if I should connect neutral to ground (I know I shouldn't do that). I'm asking if I should connect all the neutrals together and pigtail off that or just treat each switch independently on the load side.

Is there a standard way to do it?

Best Answer

If you have an electrical box at the second switch bank location with enough cubic inch volume you should really keep each circuit separate (i.e. not inter tie the neutrals). The primary reason is that you want the current in the hot line (in this case the travellers) and the neutral of each cable to be the same.

Another good reason for that would be that at some time in the future it may be desirable to bring an alternate power feed to the first switch bank location to feed one lighting circuit separately. You do not want to intermix the neutrals from two separate circuits.