Electrical – Crimp spade connectors in breaker box

circuit breakerelectricalelectrical-panelwiring

I am installing an Eaton CHSPT2ULTRA surge protector to my Siemens QP breaker box.

enter image description here

enter image description here

The surge protector has (4) 14-gauge stranded wires to connect. I had no problems making a tight connection with the green wire to the grounding bar, and to the white I added some stranded 10-gauge wire with a wire nut to reach the neutral bar, which is secured tightly.

The problem is that the black and red wires connected to the 50 amp breaker don’t seem too secure. If I tug on the wires somewhat they don’t come out, but I think if I pulled harder I could pull them out of the breaker without too much effort.

enter image description here

Taking a close look at the 50 amp breaker, it’s (of course) made for a much larger (8-gauge) wire. Even with the screw all the way tight, there is still space at the bottom of the screw. So it seems to me that the 14-gauge stranded wire just isn’t big enough for the breaker screw to hold the wire tightly.

enter image description here

What is the best way to fix this loose connection at the breaker?

  • Can I use crimp-on spade terminals to the two breaker wires? Is it up to code to have this connector inside a breaker box? Gardner Bender makes a 16-14 AWG 4-6 Stud Spade Terminal, Vinyl Blue (10-Pack) that is rated for 600-Volt maximum rating as building wiring and 1,000-Volt maximum rating for signs and fixtures, and has UL and CSA safety listings.

enter image description here

enter image description here

enter image description here

  • Is there a better way to do this?

Thank you!

Best Answer

You are correct in addressing this, but the ring terminal isn't the right tool for the job

You are indeed correct that 14AWG is well outside the listed/labeled range of the lugs on a 50A Siemens QP breaker -- they're rated for 8AWG through 4AWG wire only. However, nobody's tested them with ring tongue terminals either, so your ring terminal solution is off base. What I'd do instead is use a short length of 8AWG stranded THHN and an appropriate wirenut as a transition pigtail to adapt the 14AWG leads on the CHSPT2ULTRA to a wire size your breakers are rated to accept. (If you insist on doing this using crimped connections, you can use a suitable closed-end crimp splice instead of the wirenut, as doing the transition with a butt/in-line splice requires a special reducing splice connector, the Panduit ESV8-ESV14-Q, that isn't a hardware store item.)