After doing some yard cleanup, I realized that my panel ground wire was severed.

I went to Home Depot and was told that they only carried a temporary solution (see attached photo) and that I should seek a code compliant connector. I also talked to an electrician and I was told that to be up to code that I cannot use a connector and that I must re-run a new ground.

Unfortunately our setup would require us to run the new ground with new ground rods in a new location because the current path of the ground is no longer accessible (it's under concrete).

Can I use a "compliant connector" or do I need to run a whole new ground wire?

enter image description here

Best Answer

Here is what the National Electrical Code says:

250.64 Grounding Electrode Conductor Installation. Grounding electrode conductors at the service, at each building or structure where supplied by a feeder(s) or branch circuit(s), or at a separately derived system shall be installed as specified in 250.64(A) through (F).

(C) Continuous. Except as provided in 250.30(A)(5) and (A)(6), 250.30(B)(1), and 250.68(C), grounding electrode conductor(s) shall be installed in one continuous length without a splice or joint. If necessary, splices or connections shall be made as permitted in (1) through (4):

(1) Splicing of the wire-type grounding electrode conductor shall be permitted only by irreversible compression-type connectors listed as grounding and bonding equipment or by the exothermic welding process.

So, the compression connector you have used there is not a listed irreversible compression connector. If it was it would be perfectly legal according to the NEC.

So, the electrician you talked to was not well informed. The Code allows the grounding electrode conductor splicing if it is done correctly.