Electrical – Do I need a ground for a new 240 volt 20 amp circuit

electrical

I ran a new 240 volt circuit to operate some motorized equipment. The equipment has a 3 prong grounded 240 volt plug. My source however doesn't have a grounding strip. Would it be better to not connect the ground wire to anything on both ends.


My source is a dry transformer with a neutral but the neutral is not grounded. The building is a mower/ maintenance shed for a golf course built in the early 60's. The source to the building from the utility is 277y/480 volts mostly to run the irrigation pump. I think the building was added as an afterthought, therefore the dry transformer was added to provide power for outlets in the building. Two 480 legs and 1 supposed neutral provide power to the high side of the dry transformer. When I arrived on the scene, I discovered that the neutral is not used and is just floating. The secondary coils were paralleled to provide 120 volts only to the entire building. I since then have successfully split the coils and now have 120/240 to the whole building. So in answer to the question on grounding, I don't know if the main breaker at the meter has a good ground for the entire building or not because it is locked up(key issue?). At any rate, like I said the neutral on the secondary side of the dry transformer is not grounded and all individual 120 circuits going out from this panel have a hot leg and neutral only -no ground wires.

Best Answer

If you're in the United States, a grounding conductor is defiantly required for all new work.

If the system was installed before grounding was required, you're not required to update the system and add grounding when the code changes. However, if you add anything to the system after the code change, you must do so in a code compliant manner. This might mean bringing the entire system up to current codes, or at least enough of it to allow the new work to be code compliant.

You might be able to simply install a proper grounding electrode at the building, and use that to ground the circuits on the secondary side of the transformer. You'll have to contact your local government to find out if that's adequate, and also to have the work inspected to insure it's done properly.