Can I use a 3 wire connection (2 hots and 1 grounded neutral) to install a sub panel in a separate structure if I install a separate ground rod to the grounding bus in sub panel?
I have 8/3 w/o ground running from the main panel for an existing 240 connection in a separate shed. I plan on replacing the existing 30 amp double breaker in the main panel with a 50 amp double breaker and I want install a sub panel that would allow me to have a 240 and a 120 outlet running off a 30 amp double breaker and a 20 amp breaker in the sub panel.
If possible and appropriate, I would like to use the existing 3 wire connection (8/3 w/o ground) to make the connection from the main to the a sub panel using the grounded neutral wire to connect to the neutral bus. I would install a grounding rod and connect the grounding rod to a separate grounding bus in the sub panel. I anticipate keeping the neutral bus and the grounding bus separate in the sub panel and do not anticipate bonding these two buses.
Will this work or do I need to replace the 3 wire connection (8/3 w/o ground) with a 4 wire connection (8/3 w/ground)?
Best Answer
You can use a 3 wire feeder to supply a separate building, if...
Changing from a 30A breaker to a 50A breaker can only be done, if you also change the wires to 6 AWG. In which case you'll have to follow current codes, and install 6/3 with ground. Breakers (and fuses) are always sized to protect the wire connected to them, so you can't change the breaker size without also changing the wire size (unless you're going down e.g. 50A to 30A).
However, depending on what you're doing, you may not have to change the breaker at all. If the planned circuits in the structure are not going to be fully loaded, you may well be able to supply the subpanel with a 30A breaker. Just because the subpanel has 50 amperes worth of overcurrent protection, does not mean the supply breaker has to be 50A. Whether or not you actually need a 50A breaker on the supply, depends entirely on what the subpanel will be powering.