I know outdoor receptacles have to be GFCI, however my hot tub manual specifically says the breaker should be GFCI (does not mention the receptacle). I know there is also a GFCI near the hot tub motor as well. If the receptacle is already GFCI, does it make sense to have a GFCI breaker as well, isn't that a waste? I suppose I could only use a GFCI breaker and not a GFCI receptacle outside, but inspectors seem to frown on that and it's a pain to reset all the way in the basement if there's ever an issue. I'm in New York State USA.
Electrical – Does an outdoor hot tub receptacle and breaker both have to be GFCI
electricalhot-tub
Related Topic
- Electrical – Dead GFCI outlet(s), wire is live
- Electrical – Tripped GFCI protected receptacles
- Electrical – AC power leaving the circuit breaker, but no AC power to AC power supply line in bathroom (and this bathroom is head/lead in daisy chain)
- Electrical – Problem with GFCI at start of circuit with both lights and two receptacles
- Wiring – 230v GFCI spa with 115v spur
- Electrical – Test button on GFCI breaker does nothing
- Electrical – Hot tub wiring plan – does the plan check out
Best Answer
GFCI is not a receptacle or breaker. It is a zone of protection provided by the GFCI device. It protects everything down the line from the GFCI device.
Sometimes the GFCI device itself has a couple of convenience outlets that are on the protected side: a GFCI+receptacle combo device. This is what you mean when you casually say "GFCI", because this is the most visible form of GFCI device.
You are also familiar with the GFCI+circuit breaker combo device. This obviously protects loads downline, since it has no convenience outlets of its own, just two "LOAD" terminals. GFCI+breaker combos are $40-ish.
Then there is the GFCI-only (not a combo) device, a "black box" which does only the GFCI function. It has two LINE inputs, two LOAD outputs, and that's all. It typically comes in a rather familiar looking package, hence the slang term "deadfront". Deadfronts are about the price of the cheapest GFCI+receptacles since they don't need child-safe sockets nor outdoor rating, around $15-18.
Since this is a dedicated circuit for 1 appliance, you also need a single plug. Common and $5 in plain sockets - rare and expensive in GFCIs.
Why do we care where we protect?
* Siemens makes breakers specifically for Square D QO panels; and UL lists them for QO panels only (they don't fit Siemens panels). However they are not any cheaper than Square D's QO breakers, so these "classified" breakers are a waste of time. So Don't mix and match brands, even if they "seem to" fit.