Electrical – Does this main service panel require blocks opposite main breaker

electrical-panel

This Murray Model 18 is the main 100A service panel to a residence in the U.S. It uses Cutler-Hammer BR-style breakers.

I'm confused because the panel cover blocks the two bus slots on the top right, next to the main breaker, and the cover there doesn't even have knock-outs like the other slot covers. Is there a rule or reason why breakers should not be put in either of those slots?

Main service panel

Label inside service panel

Best Answer

No, you can't

Since your panel isn't listed and labeled to have a breaker put there (the wiring diagram on the panel label would show a set of usable spaces there if they were intended to be used), it can't have a breaker put there (not without violating NEC 110.3, that is). You'll have to find a different way to fix the space problem (perhaps with the aid of double-stuff breakers?)

While you're in there...

You also have a fairly minor alien problem -- the panel's a Murray LC120 and is only listed and labeled for Murray MP breakers as a result. (Newer Siemens/Murray panels are cross-listed for MP and QP, but yours is too old for that.) So, you'll need to replace that BR tandem with a MP2020 and move it to one of the bottom four slots of the panel (as it's currently in a place that violates the panelboard labeling due to CTL issues), while replacing the other BR with a MP120 or an Eaton CL120 (which is UL classified for use in a Murray panel).