I am having a grain bin erected and need to power it.

I have a 100 amp service at the pole. The grain bin in 250' away from the pole.

I will have a second grain in built next year right next to it. So, I'd like to size the wire to run it once or run a pair of feeder wires so I don't have to come back next year.

Each grain bin consists of the following:
1) Fan with a 10HP, 230v single phase
2) Unload auger with two identical motors – 7.5hp single phase 230v

Grand total, I'll be powering two 10hp and four 7.5hp.

What wire do I need to run from the pole to the bin(s)?

Best Answer

Your worst case scenario on the SERVICE is the 2 x 7-1/2HP 230V single phase motors on one bin while being unloaded, with the 10HP on the other one running the blower. 7-1/2HP 230V single phase motors are 40A each, the 10HP is 50A. You have 130A of load here. You cannot run that on a 100A service, continuous or not. So the wire size is moot.

But IF you get your service upgraded to let's say, 200A when you get the 2nd bin installed next year, then ASSuming you have a separate run from the service panel to each bin, the max worst case load would be 80A on each run, conductors must be 125%, so you size for 100A. You would need #3 Copper cable (if you can even find it), or #1 Aluminum, before de-rating for voltage drop (which I'm not going to do for you) so I would go one size larger.