I live in an older home I bought 2 years ago. It was built in 1924. While becoming familiar with the electrical system I discovered the circuit powering the heating furnace, from a 20 amp CB in the main box. As I traced the conduit to the gas furnace I found "power switch" box that contained 2 olde-fashion fuses.

Circuit Diagram

When I opened the fuse/switchbox I found 2 fuses. A 30amp & a 15amp. Is this correct? Seems to me the fuses should be the same rating, right? Is 2 30amp fuses correct considering that the CB Box breaker is rated at 20 amps? Thanks! Dave

Fuse/Switchbox

Here's the CB in the box. 20amp 120v. 20amp CB in Main Box

Here is the fusebox with door closed. Not sure what the text means. Is it possible that prior to the currently installed gas furnace there was a 240v electric furnace that was protected by this fusebox? And then when it was changed to gas they used the previous 240v wire for the 120v line needed? Fusebox Closed

Here's the furnace name plate. Furnace Name Plate

Here's the Gas Furnace Manual title page with the model number, etc. Manual Title Page

I found this wiring diagram. Wiring Diagram #1

Here's another diagram. Another Diagram

Here's the 3rd diagram. 3rd Wiring Diagram

Best Answer

Background: The 20A fuse is a Type S, meaning it is a "time delay" type fuse that allows things with motors to get to speed without making the fuse blow. The 30A fuse is a Type W with is not time delay, it is a "fast acting" type of fuse.

Best guess... The furnace originally had Type S 20A fuses, but something was wrong so fuses kept blowing and after getting frustrated (but not finding out why), someone just put a larger Type W fuse in there so that it would not blow. Totally the wrong thing to do and is one of the biggest problems with fuses, which is why they are not used in houses any more.

Some time later your house was upgraded to using circuit breakers (circuit breakers would not have been used in 1924) and the installer wisely put a 20A breaker on that circuit, rendering the fuses irrelevant (assuming the wire is 12ga or larger).

But... here's another potential problem. Your drawing seems to imply that there is a 1 pole 20A breaker on the one wire feeding this, then the photo seems to show that there is a fuse (the 30A) on the white wire, which would be typically indicating the neutral circuit. It is illegal and DANGEROUS to have a fuse on the neutral circuit! If the breaker is 2 pole and this is a 240V circuit going to the furnace, then it's fine, other than the use of a white wire (white is only to be used for neutral circuits).

If none of this makes sense to you, I suggest getting a qualified electrician to look at it and, if possible, just remove those fuses.