I have a 70s kitchen with a very long countertop. I understand that I only need one GFCI to protect the downstream outlets (for example near the sink). However, I decided instead to install 3 separate GFCIs, by using pigtails going into the line connectors on each unit. While it may seem redundant, my goal is to make it convenient and clear for anyone in the house to understand which outlet tripped. My question is whether this is an okay setup. 20a circuit for 3 of the. 12-2 wire.
Electrical – have multiple GFCIs on one circuit
electricalgfci
Related Topic
- Electrical – Confusion regarding 2014 NEC
- Electrical – Do I need two separate duplex receptacles for dishwasher (GFCI) and garbage disposal
- GFCI Outlet or Breaker
- Electrical – How to find the bathroom’s GFCI
- Electrical – Bathroom light tripping GFCI
- Electrical – Replacing receptacles protected by one GFCI outlet
- Electrical – 15 amp line connects to -> 20 amp line -> 20 amp GFCI -> 15 amp outlet
- Electrical – Wiring for GFCI with 3 cables
Best Answer
Yes, it is OK, assuming your work to pigtail everything is done correctly (hot, neutral, and ground all pigtailed, with the box also grounded if it is metal). You can test each receptacle individually with others in on and off states to be sure.
I assume your location is North America based on the circuit capacity and nomenclature used for wire sizing.