I have seen answers to similar questions but not sure they address my situation. I recently "installed" 2 separate 20A circuit runs for a dishwasher and a garbage disposal respectively (overkill perhaps). I will be installing a switch between the breaker and the garbage disposal receptacle next. I will then install the receptacle underneath the kitchen sink where the garbage disposal and dishwasher will plug in. I believe I have read that NEC 2014 requires GFCI for a dishwasher but not for disposal (seems backward to me but okay). If so, does this mean I should install a 2-gang box with one GFCI duplex receptacle for the dishwasher and then one standard (or another GFCI) duplex receptacle for the disposal? Can I use one GFCI duplex receptacle for 2 separate circuits?

Best Answer

Yes, you are right. Current code wants the dishwasher GFCI protected. However, unlike the dishwasher, there is no specific article that explicitly states a disposal requires one.

A Double pole GFCI 20 Amp breaker can protect two individual appliances. The Wiring is known as a MWBC "multi-wire branch circuit" and uses 12-3 "Black, Red, White, and Ground".

However, current code also wants everything in a kitchen, including dishwashers to be ARC-fault protected. One solution is to use a Double-Pole Dual GFCI/ARC fault 20 Amp breaker.

enter image description here

But since you ran two separate branch circuits I don't think code allows you to combine the neutrals as one in the panel because the conductors are not in the same sheath/raceway when they leave the panel. In which case, you would just do as you mentioned using a 2-gang box with one GFCI and one regular outlet, which is probably far way less expensive!