I plan to install a sub-panel for my woodworking shop, and would like to determine the total capacity that should supply that sub-panel. These are the main items that will likely be running in the shop, possibly simultaneously:
- table saw, 240v, 14 amp
- dust collector, 120v, 9 amp
- freezer, 14 cu ft (I don't have the amperage)
(The lights are run on their own circuit.)
What is an appropriate capacity for the sub-panel?
Best Answer
It's all about Volt Amperes.
NEC 2008 gives us an easy way to do things in residential.
So we can use 220.82 (B)(2) to figure for the dust collection, freezer, and an additional circuit for receptacles.
1500VA * 3 = 4500VA / 120V = 37.5 Amperes
You'll then have to use the values from the nameplate on the table saw to figure for that (A Volt-Ampere value should be listed on the nameplate, use that number for more accurate calculations). You could also use this method for the dust collection system and freezer since they are both "permanently connected, or located to be on a specific circuit".
3360VA / 240V = 14 Amperes
Now we'll add them up.
37.5A + 14A = 51.5A
So This is what our subpanel will look like.
Notes:
Don't forget to balance your loads between the two legs in the subpanel.