All conduit has a fill rating (which equates to 40 % of the free area full of wire, unless there are only 1 or two wires - in practice, less fill is better - the full-rated fill is VERY hard to pull into conduit. That is slightly different for different type conduits due to the different actual size of the hole in the different types of conduit. There are charts in the NEC, and there are also a LOT of on-line conduit fill calculators (and some charts.)
You're in conduit, use individual wires - they are cheaper, they pull easier, and the conduit fill on cables is terrible.
Typically we shoot for less than 3% voltage drop at rated current. Less drop is OK.
I'm fairly sure you need 6Ga wire minimum for a 60 Amp feed - given a short 30 foot run, this is also probably perfectly adequate. I'm getting 1.8% drop for 60 amperes at 240V on 30 feet (one way) of 6 Ga. Edit - Copper!
The limiting temperature rating if using THW, THHN, etc wire is generally the temperature rating of the connectors on the service equipment (breaker or panel) which is usually 75 C - even if using 90C wire, you have to follow the 75C section of the table due to the connections.
Copper .vs. Aluminum.
Copper (Cu) costs more, Aluminum (Al) less.
Copper has better conductivity - effect being, smaller wire to carry the same current. In this case, 6 gauge copper .vs. 4 gauge aluminum.
Copper oxides are conductive. Aluminum oxide is an insulator, forms quickly, and sticks very tightly to the wire. Aluminum connections need special procedures and materials to make a solid connection that won't get loose over time and overheat. These include things like brushing the wires with a stainless steel brush and an aluminum wire connection compound that coats the wire to prevent contact with air. The connections themselves must be rated specifically for use with aluminum, but most large ones will be (generally marked Cu-Al meaning they work with both, where unmarked connectors are assumed to be copper wire only.)
Aluminum connections are further complicated by cold flow, but that gets long and complicated to get into, and is supposed to be addressed by using the proper connector types. Essentially the connection gets hot, the wire swells, the swollen wire deforms, the wire shrinks, the connection gets looser, so next time it gets hotter, repeat until fire.
Best Answer