Electrical – If using an old 240v cable to make two 120v circuits, is there a risk of overheating the shared neutral return

electricalvoltagewiring

I've seen discussions of using an old 240V wire (two hots, a neutral, and a ground) and reconfiguring it to have two 120V circuits.

As an example, if it is a 20A cable, you could have two 20A circuits, each one using one of the two phases and both sharing the neutral and ground.

If each circuit is powering a device using the full 20A, would this result in 40A of current going onto the neutral, causing overheating?

Additionally, will sharing the neutral cause interference between the circuits?

Best Answer

Actually, it would result in a net 0 A on the neutral. So this actually can work quite well and is called a Multiwire Branch Circuit or MWBC.

The one catch is that the breakers powering the circuit need to be set up for common shutoff - i.e., if you turn off one, you always turn off the other. If the breakers are actually set up for common trip, which is normally the case for a 240V circuit like a stove or dryer, then that provides common shutoff as well.