I have an electrical panel in my garage with a single row of breakers 4 single 15A breakers installed and 4 blank spaces left. (pretty certain it is a sub-panel off the house) It has a sticker that says 70A max. Am I able to install a 50A 240v breaker in the spaces left over?
Electrical – install a 50A breaker in a 70A sub-panel with other breakers installed
circuit breakerelectricalelectrical-panelsubpanel
Related Topic
- Can/should I replace this 50A breaker with a 15A breaker
- Running 2nd sub panel from 1st sub panel
- Electrical – AFCI breakers in a Main Panel installed and tripping immediately with neutral pigtail connected
- Electrical – Seeking advice on how to rearrange existing breakers and add 2 circuits, including a 20A GFCI/AFCI breaker in a split-buss GE panel
- Electrical – put the sub-panel for the attached garage in the attic
- Electrical – Garage upgrade from 20 AMP to 50 AMP
- Electrical – Should I Install a sub-panel, IN PLACE OF of an unused hot tub disconnect, for a basement project, and will I need to change the main breaker
- Electrical – Are there safety concerns or code violations with the garage sub-panel
Best Answer
There is not enough information to give a yes or no answer. The breaker that supplies this panel and the wire size would be needed to say if it would work. Can a 50 amp breaker be installed in a 70 amp panel yes. Can this be done if the total of all the breakers add up to more than the panel rating? Yes but the over current protective device (breaker) feeding the panel can not be more than 70 amps. One easy example would be for a heating and cooling sub panel lets say 60a of electric heat and a 30a AC unit total 90 amps but it is legal because only 1 load would be used at a time. So in short a 50 amp breaker can be used in a 70 amp panel but if your breaker feeding the panel or the wiring is not sufficient size it won't work.