Electrical – install a 60A main breaker in a load center rated for 125A

circuit breakerelectricalsubpanelwiring

Following my previous question about feeding a sub-panel…

I have access to a new-in-box 125A load center, which is more current than I need, but the form factor is good. Can I drop to a 60A feeder wire and breaker setup without running into any obscure code-related incompatibilities? What additional hardware do I need to install the main breaker since this one is "Main Lugs Only"?

enter image description here

enter image description here

enter image description here

Best Answer

Yes you can get a 60A main breaker for this panel

Your panel uses what is known as a QOM1 main breaker frame size -- this is standard for Square-D panels up to 125A. While an ordinary Homeline 60A breaker won't fit there, the good news is that Square-D does make a QOM60VH -- so simply install that into your panel as per the supplied instructions, and you'll be golden as far as your main breaker goes. (Some other panel makes would require you to use Harper's approach of using a backfed branch breaker for the main, instead.)

You'll also need a PK15GTAL ground bar or two, as this will be a subpanel instead of a main panel.