Electrical – Instant water heater wiring

electricalelectrical-panelwiring

I'm installing a new instant water heater. The unit requires a 6 gauge wire when there was only a 14/2 (undersized?) wire going to the previous boiler-style hot-water heater. The electric panel is in the garage roughly 40ft away straight shot through the attic.

Now I don't fuss around with the breaker panel (I'll hire an electrician for that). I mainly have two concerns. Can 6/2 wire like this be run in the wall, namely the stretch from the attic down to the heater which is in a closet and down to the breaker from the attic.

And also, do I need a subpanel? Or can the 60amp breaker be installed in the master panel and the 6 gauge wires be connected in some kind of enclosure using a 6 gauge terminal block to the conductors of the water heater?

Best Answer

You can use that 6/2 WITH Ground wire and run it down through the stud just like 14/2.

I am surprised that it requires 6 gauge wire - What voltage and how many amps ? I know you mentioned a 60 AMP breaker but that does not tell unit amperage as there are codes and guidelines for proper CB ratings.

That has to be one serious Hot Water Heater - I would have expected #8 or #10.

As for your mention of 14/2 to the boiler unit:

  • Any chance your old unit was a gas unit ?

That would explain the 14/2 wiring 120VAC for control circuits and gas to do the heavy lifting.
Just an FYI they do make Gas Powered Instant Water Heaters as well.

A 60 AMP breaker might be fine in the same panel as long as your panel will support the additional load. Since you are calling an electrician get quotes an electrician will tell you if your panel will support the added load or if you need a sub panel. This is all dependent on what you already have - a panel model number with pictures of behind the face plate cover would be helpful.

Since your Instant Water Heater is 220V you will not need an AFCI breaker, I would recommend a GFCI breaker.