Electrical – Is home wired correctly

circuit breakerelectricalelectrical-panel

After looking at it more carefully:

  1. So it looks like the 30 amp breaker with the 14 gauge wire is to the garbage disposal.
  2. The AC is wired the a double pole 20 amp with 14 gauge wire.
  3. The two single pole 15 amp on the bottom right (red and black) are spliced together (wire nuts) to two wires coming from the same metal conduit, two wires but are both black.
  4. Ground and neutral wires are connected to the same bus bar in the same slot.
    These things seem odd to me…

Image 1

Image 2
Image 3
Image 4
Image 5

Updated with more pictures.
Image 6
Image 7

Best Answer

Easy. For each wire, determine if it's 10 AWG, 12 AWG, or 14 AWG wire. Then consider the following table:

  • 14 AWG, 15 amp breaker
  • 12 AWG, 20A breaker
  • 10 AWG, 30A breaker

Don't upsize any breakers. But if the breaker is bigger (in amps) than the wire in the above table, downsize the breaker. BR breakers cost $5 for a single and $10 for a double.

Any wrong-type breakers (looking at you Square D), replace them.

If any cables have 2 hots (e.g. red-black-white Romex) get a 2-pole breaker of appropriate amperage and land both hots on the 2-pole. Note a 2-pole is not a duplex. A 2-pole is twice the size of a normal breaker.

That's it. You're done.

After this, some loads may trip the breaker. If that's the case you'll have to follow the usual troubleshooting - too many loads on one circuit, too small cable needed, etc.

If a breaker serves only one motor load, ask a new question with the motor specs and ask whether you can use (size of wire you have) with (size of breaker you used to have).