I've got a circuit in the basement carrying a handful of outlets. This circuit has no ground wire. I want to add a couple of outlets and want them to be grounded. I may even want gfci outlets on them in the future. I have no reasonable way of getting a ground wire to the panel but I do have easy access to another circuit that does have a ground wire. Is it acceptable to borrow or share a ground wire between circuits? If not, why not?
Both circuits are 20A with 12 AWG wire.
Best Answer
Yes, in most jurisdictions.
NEC 2014
The 2014 version of NEC has made a change to 250.130(C), which now allows you to connect to the equipment grounding conductor of another branch circuit, as long as it originates from the same enclosure. The new text reads as follows:
So if your area has adopted NEC 2014, you can connect a grounding conductor to the grounding conductor from another branch circuit, as long as both circuits originate from the same panel.
NEC 2011
Depending on what code has been adopted in your area, you may not be able to borrow the grounding conductor from another circuit.
Here is what NEC 2011 has to say about replacing receptacles with no equipment ground.
Which means you can add a grounding conductor, but only at or before the service panel.
NOTE:
The grounding electrode system (of which the grounding electrode is a part), dose NOT include branch circuit equipment grounding conductors. The grounding electrode system is a collection of conductors used to connect the service equipment to earth, and is typically located at or near the service entrance only.
More from the NEC
There's a good YouTube video, where Mike Holt explains the options for Replacing two-wire receptacles
Consult your local government and/or a licensed electrician, to determine which version of code is used in your area. Codes do change, and you'll always have to follow the code adopted in your area.