I understand running the neutral wire back to the main service panel and not bonding the subpanel… but running the equipment ground back to the main panel seems to get conflicting answers.

If code requires it, then I'm assuming it's because the main panel should be adequately grounded but is it against code to also install a ground rod at the subpanel just to be safe? If the subpanel is mounted to a metal stake or metal building wouldn't it be grounded anyway?

Talking to different so-called experts some say on a long run to a subpanel just install a ground rod at that location and save the cost of a fourth wire.

Best Answer

To make this easier, consider the grounding conductor (the ground wire) as a backup neutral. It's not used unless a ground fault occurs, in which case it's only purpose is to provide a path back to the source so that a protective device will trip. (breaker, fuse, etc.)

Your grounding electrode system on the other hand, the ground rod here, is only used for over-voltages on the line such as static or potentially lightning. Although we bond the grounding system, they serve two different purposes.

So for your first question: no, it is not against code to install a ground rod at the subpanel. It is actually required by code.

NEC 2014 - 250.32(A)

Grounding Electrode. Building(s) or structure(s) supplied by feeder(s) or branch circuit(s) shall have a grounding electrode or grounding electrode system installed in accordance with Part III of Article 250. The grounding electrode conductor(s) shall be connected in accordance with 250.32(B) or (C). Where there is no existing grounding electrode, the grounding electrode(s) required in 250.50 shall be installed.

The only exception to that being that if you were only running a single circuit (or multiwire branch circuit) with a ground wire, then you would not need an electrode system.

Now on to your next question on if a metal stake/metal building works as an electrode: yes and no. There are a few conditions were these could apply, but they do have to have direct contact to the ground (the earth itself, the dirt or concrete below). Check out 250.52 (NEC 2014) for the list of electrodes that can be used.

Lastly, all new feeders to outbuildings must contain a ground wire. Previously they were not required, but this is no longer legal or up to code for new installations. However, modifications to existing 3-wire systems do not require the pulling of a new ground wire as long as it fits a few requirements for the exception; as seen in 250.32(B) (NEC 2014)