You're going to have to either get a washer that accepts 240V, or change the circuit.
New Washer
Getting a new washer will depend on the manufacturer, dealer, and other factors that are off topic here.
Change the circuit
Modifying the circuit will require knowledge of electrical safety practices, and general electrical wiring principles/standards/codes. If you lack this knowledge, or are not comfortable working with electricity, please contact a local licensed Electrician.
If you decide to tackle this project yourself, here is an overview of what needs to be done. You'll be going from a configuration with two ungrounded (hot) conductors, and one grounding conductor (NEMA 6-20). To a configuration with one ungrounded (hot) conductor, one grounded (neutral) conductor, and one grounding conductor (NEMA 5-20). To do this you'll have to swap out the double pole breaker for a single pole breaker, and repurpose one of the conductors.
At the Panel
- Before you begin, you'll need to purchase a 20A single pole circuit breaker that is compatible with your service panel, and a blank panel cover insert.
- Start by turning the power off by flipping the main breaker to the
OFF
position, then verifying that power is off using a non-contact voltage tester.
- Remove the service panel cover (be careful working in the open panel, the main lugs are still energized even when the main breaker is in the
OFF
position).
- Locate the breaker for the washer.
- Remove the wires connected to the breaker (should be either black & red, or black & white).
- Remove the breaker from the panel.
- Install the new single pole breaker in one of the slots where the old double pole breaker was.
- Install the blank panel cover insert in the panel cover, so that is covers the empty space left.
- Connect the black wire that you removed from the breaker in step 5, to the new breaker.
- If the other wire from step 5 is white, connect it to the grounded (neutral) bus bar. If the wire is red, mark the wire with a bit of white tape, or a white marker, then attach it to the bus bar.
- Reinstall the panel cover.
At the receptacle
- Before you begin, you'll have to purchase a 125V 20A receptacle.
- Uninstall the old receptacle.
- Connect the black wire to the brass screw terminal on the new receptacle.
- If the other wire is white, attach it to the silver screw terminal on the new receptacle. If the other wire is red, mark it with white tape or a white marker, and attach it to the silver screw terminal on the new receptacle.
- Attach the bare or green grounding wire to the green grounding screw on the new receptacle.
- Mount the receptacle in the box, and install the cover plate.
Once everything is finished, you can flip the main breaker, and the new breaker to the ON
position.
WARNING:
This answer is only applicable in the US, and possibly Canada.
A quick search indicates that acquiring 3 phase power from a local utility may be prohibitively expensive. The article I read suggests that such a resource will carry an installation expense in areas not rated for commercial service and may also carry a minimum charge on the utility bill.
If your objective is occasional use of heavy equipment such as a machine tool, it may be more practical to use a device called a rotary converter. You would want to ensure your selected device has the necessary capacity for your expected load maximum, with a bit of reserve tossed in for good measure.
If only a single machine is going to be using 3-phase power, another device known as a VFD would be of value. A VFD will provide variable speed to an otherwise single speed motor as well as other features one can determine by searching for that term.
There are plans online to build your own rotary converter. A friend without internet access, many years ago, connected two motors together via belts, powering one with line current and used the gizmo to run a monster Czech lathe in his shed. He had to "kick-start" it periodically by kicking one of the pulleys, but it worked. I'm sure a commercially produced version would not require such manual intervention.
The above assessment was performed based on a US installation. Other countries may have different circumstances.
Best Answer
Besides switching which outlet it's plugged into you can instead put a meter on the washing machine while it's permanently plugged into the grid of one of the floors and then have the owner of the other floor pay half the cost every so often.