Electrical – PV inverter breaker sizing requirements

electrical-panel

I have a PV inverter that is rated at max output of 25A, and the backfeeding breaker in the main panel is a 35A. This is appropriate considering the 25A * 1.25 and round up sizing formula. However, I'd really like to move an additional size up to a 40A breaker so that I can replace the existing one with a quadruplex breaker to free up a space in the panel.

The main panel is rated 200A so I should be allowed up to a 40A PV breaker. The conductors to the inverter are #8 THHN in conduit.

Is there anything that should prevent me from swapping this 35A breaker out for a 40A quadruplex?

Best Answer

Short answer. Your fine to upgrade to a 40A breaker. Remember the breaker is being used to protect the feeder conductors. If you feel you need to use the breaker to protect your inverter you should install protection just before the unit.