Electrical Question about a 100 amp sub-panel to a 100 amp sub panel in the out-building

electrical

O.K. I ran the appropriate wire from my sub-panel to a sub-panel in my 'out-building'. I stopped by the electrical supply house and spoke to an electrician for the correct wire size for that process…

QUESTION: When I put in the 100 Amp breaker in the 200 Amp Main Panel and run it to the 100 amp breaker in my sub-panel to the 100 amp service in my 'out-building', the wire connections in the breakers are NOT that large. So, what size can I use that would be appropriate….

Best Answer

I'm with Kris. A 100A breakers lugs are sized for a #4 through a 1/0 which is one size larger than the required #1 aluminum. I guess what you are saying is that you have run an over sized feeder.

Since you have already run the feeder you might need to reduce the conductor to fit the breaker lugs using an insulated butt splice, like the picture, inside the panel.

enter image description here

Good Luck