Electrical – Repurpose unused 50 amp hot tub panel for 30 amp hvac

electricalelectrical-panelhvac

I have a sub panel that was from when the previous owners had a hot tub.

enter image description here

I'm currently needing a 30 amp circuit for a mini split system and was wondering if I could just swap this 50 amp breaker and then run my 10/2 ** ( correction 10 gauge wire) ** in place of the 6 gauge wire that's currently in place?

I know I could run a sub panel from this panel or replace this with a small panel and have the advantage of expanding things in the future. However I can't see any scenario where I would ever need that.

** Update For Clarification **
The conduit and 6 gauge wire that was feeding the hot tub would remain in place just be capped and disconnected in the box. I would punch a new hole and run the new conduit and 10 gauge wire about 10 feet from here to the outside condenser.

Best Answer

You can do that. You will have to pigtail a piece of #10 cu to the #6 because the #6 won't fit into a 30 Amp breaker. I would replace the breaker in your main panel and do the pigtailing in there. Then replace this breaker box with a 30 Amp disconnect switch with separate neutral and grounding bars. This breaker is an old Challenger breaker and they have been known to be fire starters. I think it's a stabloc but I'm not sure. Hoping one of the big three will chime in if I'm wrong.

Ok we've got confirmation it's not a Stab-Loc. I'd still replace it with a disconnect.