Electrical – Should I avoid ground loops in branch circuits through conduit

electricalgrounding-and-bondingwiring

I've got some outdoor conduit within which are three separate branch circuits:

  1. A general purpose, 20A outdoor receptacle circuit
  2. A 15A HVAC circuit
  3. A 40A EVSE circuit

I am using NM-B for each circuit on the indoor segment that connects the breaker to the conduit, at which point I transition to THWN. The NM-B has a ground wire included, and I know that I only need to ground the conduit to the 8AWG wire from the EVSE circuit. My question is, should I not connect the ground wires on the 15A and 20A circuits to avoid creating a ground loop, or does it not matter?

Best Answer

The "ground loop" in question does not matter one bit -- the NEC assumes all involved EGCs are connected together at all junctions, even. (It's impossible not to have them all connected together in a metallic conduit system, for one.)

Note that there are a few exceptions for isolated grounds for certain sensitive equipment, but the benefits of isolated receptacle EGCs are unclear. (Note that the redundant earthing requirement in patient care areas is not an isolated equipment grounding requirement!)