Electrical – Sub panel and neutral and ground bus bar

electricalsubpanelwiring

Some HVAC people under previous home owners put in a sub panel box and ran the AC as well as some lighting and outlet circuits from the sub panel.

The bus bars on the two sides of the panel box were used for both the neutral and the ground wires just like in the main breaker box.

I assumed that it was right because they were professionals and should have had an inspection for the sub panel and the HVAC. I have been reading about how sub panel boxes should have separate neutral and ground bus bars.

Are there panel boxes which are not designed to be sub panel boxes and should only be used as main breaker boxes? The sub panel looks like the main box except the sub panel did not have a main shut off breaker in the sub panel.

Best Answer

You are probably in violation of National Electric Code, article 250.32(B)(1) states that the grounded conductor(neutral), shall not be connected to the equipment grounding conductor(ground).

The general rule of thumb is the only point the ground and neutral get bonded together is at the first point of disconnect for any incoming system, be it utility, generator, or some other source. There are a few exceptions for specific situations but none of which I feel apply.

Easiest course of actions is to kill panel, un-bond bars, drive screw through one bar into chassis and make that ground bar, use the other isolated bar for neutral. With no other knowledge of your installation I would advise you be careful of the loose neutrals while making the swap, if any are somehow being used by circuits from the other panel(it happens) they could shock you.