You can use a clamp meter to measure current through a single conductor.
Current is the number of electrons flowing through the wire per unit time, and is measured in amperes. If you know the voltage, you can use that to calculate power (watts):
Power [watts] = Current [amps] X Voltage [volts]
If this is a standard residential power system you can assume 110V or 220V for the voltage, or you can measure it with a voltmeter/multimeter. If you want kW instead of watts, you divide by 1000. (The formula on your website includes a "Power Factor" which is based on the appliance being used. In most cases it's close to 1, so you can just leave it out unless you need to be super-precise or happen to know that you have a low power factor.)
The major limitation of a clamp meter in measuring household power is that it can only be clamped around a single conducting wire, not the entire romex cable. If you clamp around the entire cable you will get a reading of 0, since the two conductors have opposite currents and they cancel each other out. This limitation means the meter is probably only practical inside the circuit breaker box or an electrical box, where space and safety concerns may make it a bad idea.
Your ohmmeter testing has established that the switch enclosure is NOT grounded. (or you were hitting it on a painted or rusted spot). That's not a surprise given the vintage of the home. Stop measuring voltages to it... or air. It's futile.
Most likely your house originally had gas lights - that's something to think about if you have a chandelier or ceiling fan, because they often hung those from the gas line. The active, never-disconnected gas line. Isn't old San Francisco housing stock fun?
And you know those 2 wires that were never connected to anything? They're not needed obviously, so please identify them and exclude them from the following test. God only knows where they go to, and energizing power onto them could be a mistake.
If feasible, put an AFCI (Arc Fault) breaker in there. Those prevent house fires. A GFCI (Ground Fault) breaker prevents electrocutions by making sure all current going down a "hot" comes back on the corresponding neutral. Distinguishing the difference is diagnostically useful here.
Time to make a test instrument. Buy a cheapie extension cord. Grab it by the prongs, cut the cord, and throw the prongy part away (or plan your cut and use it for another project.) Strip the cut end of the cord back to expose hot and neutral.
Plug a desk lamp with an Edison base into the socket on the cord. CFLs and LEDs won't work for this - get matched incandescent bulbs. Put one in every lamp under test (remove others), plus one in the desk lamp. Get spares.
Shut the breakers off, wire-nut the leads to any two wires, have a helper turn the breaker on and see what happens. Do the same matrix you did before (leaving out the two mystery wires for now).
- If the test lamp and a fixture both light dimly, you have found a "line" and a "load". This is guaranteed to happen at least twice.
- If they are of unequal brightness, different wattage bulbs, no big.
- If the test lamp lights full brightness, you have found a "line" and a "neutral" or "ground".
- If the lamp lights very brightly, once, you have found two opposing "line" legs of 120V (240V between them). That is special, possibly a MWBC.
- If an overcurrent trips, you did something wrong, or bad wire.
- If a ground fault trips, it means you have found a "line" and a "ground". Or (not likely) a "line" and the neutral from another circuit. Or bad wire.
- If an arc-fault trips, it means the wiring just tried to set your house on fire. There's a remote chance it succeeded - inside-wall fires can take hours to develop - so stay around for a few hours.
That's why I'd start with an arc-fault breaker, especially if you're messing with those two mystery wires. A dual-mode breaker is OK if it can tell you definitely that it tripped for arc-fault and not something else.
Then get back to us and tell us what you find.
Best Answer
Stay away from the 10A terminal. That is for amp measurements ONLY, and creates a dead short between the 10A terminal and the common. This will blow your fuse, burn up your probes, and/or destroy the meter. Never use that unless/until you know exactly what you are doing.