Electrical – Why would an air conditioning unit specify a maximum breaker size

circuit breakerelectricalhvac

A ductless mini split unit I am interested in specifies a maximum breaker size of 15 amps. Why would this be the case?

The unit is going to be installed on the opposite side of the house from where the breaker is, so for a 220v system that runs at about 5 amps, a 70 foot run of electrical wire calls for 8 gauge wire.

I was going to throw a 20 amp circuit breaker for this run until I came across the spec sheet for the unit. I found a similar post where the top answer states that you can always use bigger wire which only reassures me that 8 gauge wire is fine in a 15 amp breaker, but I can't seem to find why the AC unit would call for no bigger than a 15 amp breaker.

In other words, why would a device on a circuit be sensitive to the potential max amperage of its circuit

Best Answer

The unit won't be protected properly by a larger breaker

While hermetic compressors and fan motors are protected against overload by internal means, or by their drive electronics if you have an inverter-based system, the wiring of the unit still needs to be protected in case it shorts out internally. As a result of this and the fact that air conditioners universally are complex, multimotor loads, UL has taken pity on installers and inspectors and requires the manufacturer to do the breaker sizing math for us. (Otherwise, you'd have to dig into Articles 430 and 440 of the NEC and size the breaker yourself, which is a bit fiddly for a multimotor load.)

So, simply use the 15A breaker the manufacturer calls for and call it a day, although I doubt you need 8AWG wire for a unit that draws less than 10A at 240VAC. In fact, for that run, 14AWG is perfectly fine. (The chart you found is probably for low-voltage DC circuits, where voltage drop is a far greater limiting factor than at 240V.) However, there is some merit to future-proofing an air conditioner circuit, and to that end, I'd run ½" ENT as that'll get you up to 50A with THHN wire and the assumption that your panel supports 75°C terminations, then pull the 3 14AWG wires needed through it.