I got a GFCI 30amp breaker and will be putting it in for my dryer circuit. Just want to confirm I'll be wiring this correctly before actually going ahead with it.
In the red circle is the white neutral wire that is associated with the red+black wires that came from my dryer into the breaker. So my plan is to:
- Swap Black+Red onto the two load terminals on the GFCI.
- Move that highlighted neutral wire to the Load Neutral terminal in the GFCI.
- Connect GFCI neutral pigtail to neutral bar (where the original neutral was in step 2)
Does this make sense? Anything I'm forgetting? I figure i don't have to do anything with the ground (bare copper) wire.
This is the new gfci breaker for reference – https://www.homedepot.ca/product/siemens-30a-2-pole-120-240v-type-q-gfci-breaker/1000406279
Update: The dryer outlet is a NEMA 14-30. He's a picture of the wiring inside the outlet
Thanks!
Best Answer
Go for it
Since you have a full four-wire connection to a NEMA 14-30 receptacle, your plan to replace the breaker with a GFCI breaker is sound, as long as the dryer is properly configured for use with a 4-wire cord. Note that this will also let you know if your dryer has a ground fault, so you may wish to keep an appliance repairman's phone number on hand in case it turns out your dryer needs fixing.
While you have the outlet box open, it would be a good idea to take a couple lengths of bare 10AWG wire and a wirenut and use them to pigtail the box ground screw and the outlet properly, as well as changing what looks to be an improper ground screw to the correct screw, namely a 10-32 fine pitch machine or self-tapping screw (the latter is available as the Garvin GSST).