So my GFCI recently stopped working. I bought an outlet tester and fixed some outlets that were incorrectly wired. My old GFCI had power but wouldn't reset and test button couldn't be pressed. When I did press reset, it would automatically trip but power was still there. I replaced the gfci thinking it was faulty. I wired it one wire at a time, making sure it was correct. Now I have no power to GFCI but all outlets downstream work. The only outlet that doesn't work is the gfci. I tried switching wires and still not power. Any suggestions? Thanks in advance
Gfci not working
gfcireceptacle
Related Topic
- Electrical – GFCI Outlet Trips with Receptacle TEST Button, but not with GFCI Outlet Tester Tool
- Electrical – GFCI tester doesn’t trip GFCI. Bootleg ground
- What happens when using a GFCI Tester on a non-GFCI outlet
- Appliances plugged in GFCI outlet works but when plugging in the downstream outlet doesn’t
- Electrical – GFCI receptacle will not reset
- Electrical – Circuit worked briefly after replacing GFCI, but stoppped
- Electrical – GFCI Breaker – Good or Bad
- Electrical – GFCI Protected Outlet Trips with GFCI Outlet Tester, but the outlet lost power
Best Answer
The GFCI isn't broken. It is correctly detecting a ground fault or wiring problem, and tripping instantly. That's its job. The test button can't be pressed because it's tripped.
It's easy to get misguided by 2 nasty forces:
"Doing this makes it work" -- There are lots of setups that work that will kill you. "Trying things" will only lead to one of those. Stop and find out what to do. We're here to help.
"3-light testers" -- I call those a "magic 8-ball tester". The lights are fine, but the written legends tend to be misleading in old work. They are for pass-fail testing brand new construction, not bona-fide troubleshooting. Also, it's an easy tester that makes a novice think the electrical world is full of easy problems. Nope; the last guy had a 3-light tester also. The problems he leaves you tend to be hard and complicated. So doing easy fixes because the tester told you to is probably counterproductive.
I think the GFCI you removed was telling you the truth -- that one of your fixes created a ground fault. I would put the old GFCI back in, very carefully exactly as you found it. It was correctly wired; this new one is miswired, I think.
"Carefully moving wire over 1 wire at a time" fails because you are relying on physical position on the device. Different models put things in different physical positions (especially 3-way switches!). Instead, rely on screw color, markings, or other evidence.
Ground always go on a screw. A ground in a backstab is always wrong.
On a socket, the taller slot is neutral. Receptacles have silver screws for the neutral side. Neutral is always the white wire (white isn't always neutral).
Anything that deviates from the above is wrong.
It will be a step in the right direction if the