I can't find a specific answer for this situation. I know that flexible conduit can be used as a 6 foot whip for luminary and "other equipment". It can be used over 6 feet. The question that I can't seem to answer is if a whip exceeds 6 feet and needs supported every 4.5 foot span, does that include the support of the 6 foot whip.
Ie does a 6 foot whip become 4.5 feet between supports. If a 10 foot section of flexible conduit 5 feet from a building has to be supported ever 4.5 feet?
So ultimately, I am asking if a 10 foot section of flexible conduit, can span 6 feet between a building and a generator without additional support between the two?
Best Answer
The NEC doesn't define a "whip" or uses of a whip. For each raceway type the code gives support requirements and exceptions. Since you are referencing 4.5' you must be referencing Liquidtight Flexible Metalic Conduit LFMC, since Non-metallic LFNC requires 3 ft support. LFMC Section 350.30 says:
None of the exceptions allow the last 6' of LFMC as you described to not be supported. You could argue that generator vibration would require flexibility as described in Exception 2, but you may not win that argument because you may need to justify how a support would limit flexibility.