What NEC requirements apply to installing receptacle next to a tree

code-complianceoutdoorreceptacle

I will install a receptacle next to a tree. I know it must be protected by a GFCI and weatherproof. But my concern is about how to support it and how high it should be from the ground.

Where in the NEC is the information about these requirements?

Best Answer

The most important code sections to be aware of when installing outdoor receptacles, are 314.15, 314.23, and 406.8(B)(1).

First off, the box should keep water out.

National Electrical Code 2008

ARTICLE 314 Outlet, Device, Pull, and Junction Boxes; Conduit Bodies; Fittings; and Handhole Enclosures

314.15 Damp or Wet Locations. In damp or wet locations, boxes, conduit bodies, and fittings shall be placed or equipped so as to prevent moisture from entering or accumulating within the box, conduit body, or fitting. Boxes, conduit bodies, and fittings installed in wet locations shall be listed for use in wet locations.

Secondly, the cover should also keep water out even when things are connected.

ARTICLE 406 Receptacles, Cord Connectors, and Attachment Plugs (Caps)

406.8 Receptacles in Damp or Wet Locations.
(B) Wet Locations.
(1) 15- and 20-Ampere Receptacles in a Wet Location. 15- and 20-ampere, 125- and 250-volt receptacles installed in a wet location shall have an enclosure that is weatherproof whether or not the attachment plug cap is inserted. All 15- and 20-ampere, 125- and 250-volt nonlocking receptacles shall be listed weather-resistant type.

Lastly, you'll want to make sure the thing isn't laying in the mud. Depending on the Authority Having Jurisdiction (AHJ), you might get away with attaching the box directly to the tree, or supporting it with the conduit used to supply it. The proper way to do it, however, would be according to 314.23 (B). Use a stake.

314.23 Supports.
(B) Structural Mounting. An enclosure supported from a structural member of a building or from grade shall be rigidly supported either directly or by using a metal, polymeric, or wood brace.

(2) Braces. Metal braces shall be protected against corrosion and formed from metal that is not less than 0.51 mm (0.020 in.) thick uncoated. Wood braces shall have a cross section not less than nominal 25 mm × 50 mm (1 in. × 2 in.). Wood braces in wet locations shall be treated for the conditions. Polymeric braces shall be identified as being suitable for the use.

Common sense says you should install the box up out of puddles, and if you get snow in your area above the normal snow level. There are no code sections that deal with the height above grade, so use your best judgement. And never forget the most important code section of all...

110.12 Mechanical Execution of Work. Electrical equipment shall be installed in a neat and workmanlike manner.