The following diagram should help you to visualize how to wire up the three switches. In your case you may have 12 AWG wire due to the 20A circuit. Also you will substitute one of the lights with the blower fan motor connection.
Picture Credit: Taken from this web page.
Plasterboard Work
It is often possible to run a new cable between a fixture and a switch without tearing up large sections of drywall.
If you can visualize the wire going up the wall from the switch and then from the corner of the wall/ceiling to the fixture, you may be able to snake a new wire.
Cut a small hole in the ceiling in in the plasterboard immediately above the switch.
The issue will be whether the hole in the ceiling allows you a straight run to the fixture box (along or between a ceiling rafters). If not, you nay need to cut more small holes where the cable would have to cross a joist/rafter.
If it is a clear run, you may be able to run a cable from the ceiling hole to the fixture box. Then you can cut a small hole in the wall immediately below the first hole.
You also need to be able to drill through or notch the framing (without seriously compromising a load bearing wall) to allow a cable to pass through. If this is feasible, you can drop a cable down to the switch box, thread the other end through the hole or notch in the framing, and extend it to the fixture box. If you are notching or if you are drilling at less than 1.5 inches in, you need to put a special metal plate over that spot to protect the cable.
Later you can patch the small cutouts, tape over and paint.
Wiring
You can continue to use the existing cable to power one circuit and use a 14-2 cable to provide the hot leads for the other two circuits (they will all use the neutral already on the circuit. Since both wires in the new cable will be hot leads for a circuit, the white wire needs to be marked at the switch and fixture to show that it is hot.
You can find three switch units that fit a single gang box, or expand the switch box to double gang.
Best Answer
You can do it using only 12/2 and 12/3 cables like this.
Or you could use 12/2 and 12/4 cables like this.
Because there will be so many wires in the box, you'll want to get at least a 34 cu. in. double gang box. Like this one.