I bought a new single electric wall oven to replace an old one in an old house. It says it requires 20 amp and 240 volts. The old one was running on a 10 amp breaker. The wire from the breaker to oven is 10/3. Can I swap out a 20 amp breaker, and will I need to run new wire?
The old oven is so old I can't find any info on it to see if the wiring was even adequate for that. Previous owner was very "handy", so I'm not sure what has been done properly or not.
Best Answer
10/3 copper NM is rated for 30A under the NEC, so the old oven was more than adequately wired, and it will support the new oven without difficulty as well.
If you are of the unlucky type to have aluminum wire in your walls -- 10/3 aluminum NM will still handle 25A, so you will be fine.
However, the load must be considered as the nameplate load (no demand factors) per NEC Table 220.55 Note 4:
The adequacy of a 20A breaker, though, depends on whether your oven is treated as a continuous or noncontinuous load as per NEC 210.20(A):
and the definition of "continuous load" in Art. 100:
If your AHJ agrees with Tester and I that a residential oven is a noncontinuous load, then a 20A breaker is fine; otherwise, you'll have to stick with a 30A unit.