I'm wanting to upgrade my 125A, 24 space panel to 200A, 40+ spaces. I'm confident to work on the main panel, but not the main service entrance. Would I be able to add a safety switch (pic below) between the meter and panel, so that I can disconnect and have a 100% dead panel?

Are there any requirements to be aware of?

  • height/accessibility of safety switch
  • switch distance from meter and/or panel
  • proximity to gas meter

Is there a different option I should be considering, which gets me to my end goal of working on my own panel?

I'm in PG&E land if that matters. I currently have a combo meter/panel, but as part of my upgrade I'll likely need to move the meter outside. The safety switch would be inside.

200 Amp indoor safety switch

Best Answer

There's no point to adding a switch here

Since you will have to move the meter-main anyway, which'll require PG&E to cut your service drop and reattach it at the pole, there's no point in adding the extra switch you describe.

So, why can't the new meter-main go where the old one did?

Well, the NEC simply requires clear working space (110.26(A)) around the meter-main, so why can't it go in the garage? The answer lies in the fact it's a meter-main, and thus invokes your utility's distribution rules about meter location. In your case, they're found in PG&E's Greenbook, which states:

5.3.2. Prohibited Meter and Service Equipment Locations

The following locations are not acceptable for electric meters and service termination equipment.

...

F. Inside garages for single-family residences.

So, since you'll need to move the meter there, and probably use a meter-main for that job, I would simply fit a Class 200 EUSERC meter-main, suitable for overhead service, at a suitable outdoor location. Then, you can have your 200A indoor panel set up in the garage as a subpanel from the meter main.