I'm installing a new 100 amp panel and have almost run out of openings on the neutral bus bar and still have 4 more breakers to install. Can I double up on the neutral side or should I start using openings on the ground side. The neutral is bonded and this is a main service (not sub panel) I'm a bit of a neat freak with this stuff and would prefer to keep grounds and neutrals separate but not at the cost of safety.
Electrical – Is it OK to have more than one neutral wire in the same connection on the neutral bus bar on a main panel
breaker-boxelectrical
Related Topic
- Electrical – install a Subpanel (in a seperate building) using a 3 wire connection (2 hots and 1 grounded neutral)
- Electrical – terminate a ground wire to the neutral bus if the ground bus is full
- Electrical – Sub panel and neutral and ground bus bar
- Electrical – Main service electric panel has no neutral wire – both neutral and ground wires on same bar – sub panel question
- Electrical – How to connect a subpanel with neutral and ground to the same bus bar in main panel
- Electrical – Should I isolate the ground and neutral in the 30A safety switch box or keep them bonded until the sub panel it is feeding (as service disconnect)
- Electrical – How to deal with subpanel that does not have ground wire back to main panel
- Electrical – add a neutral bus bar to the panel to allow more connections
Best Answer
Neutrals must be one to a hole. No exceptions.
NEC 2011:
Since this is the main panel there is typically no separate neutral and ground bars, although additional bars that attach directly to the back of the panel box MUST be for grounds only. The metal panel enclosure CANNOT be used to carry current.
As long as both existing bars are connected by a link bar or other path you can use either side for neutrals. Grounds typically can be two and even three conductors to a hole, sized #14 or #12 and sometimes #10, and must be the same size. So if you need to make room you can double up on some grounds.
Neatness is all well and good, but fanaticism at the cost of convenience and logic is silly. Keeping the grounds and neutrals on separate bars in a main panel makes absolutely NO sense at all. IMO it is neater when all the wires don't cross from one side to another.