I have a Crouse-Hinds main load center. The ground bus is at the top left of panel and the neutral bus is at the bottom right of the panel. I want to add a 15 amp circuit for two outlets in my garage. The ground bus bar terminals are full. My question is can terminate my neutral and ground wire both to the neutral bus bar as long as they each are different terminals on the neutral bus bar. This load center is main panel and not a subpanel.
Electrical – terminate a ground wire to the neutral bus if the ground bus is full
breaker-boxcode-complianceelectricalgrounding
Related Topic
- Electrical – In a secondary panel, are grounding and neutral bus bars required on each side of the hot bus bars
- Electrical – Is this neutral-ground bus bar configuration correct
- Electrical – How to connect a subpanel with neutral and ground to the same bus bar in main panel
- Electrical – Single neutral bus bar in subpanel with 2 columns of breakers
- Ground Bus Bar on Sub Panel
- Electrical – Termination point at main panel for a 4 wire feeder ground wire to sub-panel in detached structure
- Attach the Ground and Neutral inside a sub-panel
- Electrical – Ground and neutral bus considerations when wiring a gfci breaker
Best Answer
Mixing Grounded and Grounding
If this panel serves as the main disconnect, and the grounding and neutral bus bars are bonded. Then yes, you can terminate both grounded (neutral) and grounding conductors at the same bus bar.
Notice that the bus bars are bonded using a bonding strap.
Multiple Conductor Terminals
If the bus bar is able to accept multiple conductors under some or all of the terminal screws, it should be labeled as such either on the bar itself or in the panel documentation. Terminating multiple conductors under a screw that is not rated for it, can cause bad connections, excess heating, damage to the conductors, etc.
Additional Bus Bars
Some panels are configured to allow additional bus bars to be installed. If your panel is one of them, you could install an additional bus bar and terminate extra conductors there. Other panels may accommodate extended (longer/larger) bus bars, that can be installed in place of the existing bus bars.