Wiring – 30a rv box from main panel

wiring

The 200a main disconnect is mounted under the meter on the power pole. It has spaces for 8 breakers and a neutral bus bar. The only ground I see is from a rod at the base of the pole to the meter. I've run 50' of #8 2wireuf from the 30a rv pedestal to the main in PVC conduit. The neutral and ground are separated at the pedestal. I intend to put the neural and ground on the single bus bar. The question is do I run #4 bare from the existing rod to the neutral bus bar in the main and put in 2 at the pedestal.

Best Answer

As this is at the main it would be fine to have both your neutral and ground on the same buss. an RV “park” doesn’t require an additional grounding electrode NEC 551.75.b
However 1 out of 3 of the counties I work in requires a supplemental ground at the pedestal as this a residential hookup not a park.

Make sure to have your box 2 feet off the ground or more but not over 6’6”.